Induction stove

RE my 6 amp supply. I have to issue a correction. I hadn't actually looked inside the bollard, as the site told me it was 6. It is in fact 10 and has 2 outlets. Last night someone plugged into the other outlet from another pitch, not the correct pitch (don't ask me why) and this morning it tripped. On looking into the box I discovered that the main RCD is 25A (fairly typical) there is only one MCB of 10A feeding 2 sockets.

When we can't get access to reset the trip then we are ultra cautious.

Another issue is how many volts you're actually getting as some of the wiring seems a little on light side, shall we say.
 
If you check I bet they have 2 hook up leads out to different sockets

Alf
 
If you check I bet they have 2 hook up leads out to different sockets

Alf
Funny you should say that, because they did have 2 leads, but they only connected one of them. No 3 bar heater in the awning...they didn't have an awning either.
 